Author Topic: 50hz compressor motor  (Read 897 times)
siraniko
CR2032 Battery
**

Pogi/Ganda Points: 0
Offline Offline

Posts: 20


« on: March 15, 2010, 09:03:15 PM »

mga sirs/maams,may dinala sa akin na portable air-cond, surplus from australia,compressor motor is tripping, measure ko ang ampere ng compressor, it runs at 2.2Amps then gradually increases to 10Amps after 2mins then trips.starting capacitor w/c is 35uf/450v is tested ok. ano kaya problema dito? is it the compressor running at 60hz sa power source natin o may tama na sa winding ang motor. Any idea mga masters?
Logged
The Philippine Electronics and Technology Forum
« on: March 15, 2010, 09:03:15 PM »

 Logged
Mr. D
Size C Battery
*****

Pogi/Ganda Points: 359
Offline Offline

Posts: 240


"Agta Maloko"


« Reply #1 on: March 15, 2010, 09:15:30 PM »

^ sir umaandar ba yung compressor in 2.2amps?
Logged
siraniko
CR2032 Battery
**

Pogi/Ganda Points: 0
Offline Offline

Posts: 20


« Reply #2 on: March 15, 2010, 09:26:18 PM »

yes sir,umaandar na normal, then after awhile tataas na ung ampere reading sa compressor, pag umabot na ng 10amps. magtritrip na ito, tnx for replying sir
Logged
Mr. D
Size C Battery
*****

Pogi/Ganda Points: 359
Offline Offline

Posts: 240


"Agta Maloko"


« Reply #3 on: March 15, 2010, 09:49:07 PM »

^ PM sent..
Logged
cha04
LR44 Battery
*

Pogi/Ganda Points: 0
Offline Offline

Posts: 1


« Reply #4 on: March 16, 2010, 09:20:43 PM »

malamang hinde pwede iyan dito sa atin, 60hz. Need siguro na i convert to 60hz ang cycle ng compressor. Ito ang example. nakabili naba kayo ng 50hz bulb type, made in china. Iilaw iyong bulb, hinde tatagal iyon, masisira.
Logged
siraniko
CR2032 Battery
**

Pogi/Ganda Points: 0
Offline Offline

Posts: 20


« Reply #5 on: March 18, 2010, 06:44:53 PM »

tnx sa mga reply mga ka forum, palit na lang ng compressor motor
Logged
DigitalMind
Technical People
Hydroelectric
*****

Pogi/Ganda Points: 219
Offline Offline

Posts: 3487


« Reply #6 on: March 18, 2010, 07:12:42 PM »

tatakbo naman yang 50hz na motor sa 60hz.
madami din akong power tools na 50hz. lahat dc/ac motors so far wala pa naman pumapalya.
palitan mo na lang kapag nasira na yung 50hz na motor.
Logged
greentech
LR44 Battery
*

Pogi/Ganda Points: 0
Offline Offline

Posts: 5


« Reply #7 on: March 19, 2010, 03:00:51 PM »

Ok ba ang ikot ng exhaust fan sa condenser ng aircon? o baka madumi ang mga fin ng condenser?.
Logged
siraniko
CR2032 Battery
**

Pogi/Ganda Points: 0
Offline Offline

Posts: 20


« Reply #8 on: March 19, 2010, 08:04:49 PM »

ok ung fan motors sir, ok sana kung di tumataas ung ampere reading ng compressor motor after 2mins. ok na ung portable air cond mga sir, napalitan na ung compressor motor.tnx sa mga replies nyo.more power sa forum!
Logged
TinTopHack
Lead Acid Battery
*******

Pogi/Ganda Points: 138
Offline Offline

Gender: Male
Posts: 702


Nothing gold can stay. - Robert Frost


« Reply #9 on: March 23, 2010, 01:07:57 AM »

Additional info lang:

Generally it is OK to operate a 50Hz motor at 60Hz but it will run with lower torque.
A motor is an inductive device. Running a 50Hz motor at 60Hz means lower operating current
because the inductive reactance (impedance) of the motor at 60Hz will be higher. Since torque
depends on current, lower current means lower torque.

On the other hand motors rated at 60Hz could have problems when operated at 50Hz because at lower freq, the inductive reactance is lower so current is higher. While higher current may mean higher torque, the motor could overheat due to this higher current. (unless the motor is designed to handle such higher current - thus some motors are rated 50/60Hz)

For this reason, variable freq drives for motors has to maintain the volt-hertz ratio to maintain
rated torque at different speed settings.
Logged

The world, as everybody knows, is analog; unless, of course, it's digitized.
brian_po
Lead Acid Battery
*******

Pogi/Ganda Points: 37
Offline Offline

Gender: Male
Posts: 882


Babaero ka ah


« Reply #10 on: March 23, 2010, 09:13:13 AM »

For this reason, variable freq drives for motors has to maintain the volt-hertz ratio to maintain
rated torque at different speed settings.

yan ang design ng inverter type models ng A/C ngyn..
na mi-mislead kasi akala ng iba "almost" pag sinabi inverter A/C eh kala nila DC supply ang motor.
correction lng.. 1ph AV power supply then converted to 3Ph A/C supply to motor compressor..
variable speed ang compressor and design to with-stand 40Hz -60Hz Freq.. depends on the requirements of the heat loads
Logged

-Conserve Water; Drink Beers
-Yesterday I did not even know how to spell engineer, today I am already one...
-LORD, Ty sa mga pagsubok na binibigay mo para maging handa ako sa mga biyayang darating..
rdpzycho
Technical People
Solar Power Satellite
*****

Pogi/Ganda Points: 466
Offline Offline

Gender: Male
Posts: 9158


Perfection is an Illusion


WWW
« Reply #11 on: March 23, 2010, 12:08:32 PM »

yan ang design ng inverter type models ng A/C ngyn..
na mi-mislead kasi akala ng iba "almost" pag sinabi inverter A/C eh kala nila DC supply ang motor.
correction lng.. 1ph AV power supply then converted to 3Ph A/C supply to motor compressor..
variable speed ang compressor and design to with-stand 40Hz -60Hz Freq.. depends on the requirements of the heat loads

OT: nakasanayan kasing i-associate ang inverter sa Battery to AC output. but basically, an inverter is a device that converts DC to any AC. so 'yung mga aircon is 1 phase AC to rectifier - DC output - single phase/three phase AC output.

mas matipid sa kuryente ang inverter types dahil pwedeng i-adjust ang starting current, then pwedeng magpalit ng speed/torque on demand. same din sa inverter type water pumps.
Logged

‎"Keep on starting, and finishing will take care of itself."

- Neil Fiore
brian_po
Lead Acid Battery
*******

Pogi/Ganda Points: 37
Offline Offline

Gender: Male
Posts: 882


Babaero ka ah


« Reply #12 on: March 23, 2010, 01:53:56 PM »

^automatic na sya mag-cha-change ng speed depende sa ma measure ng sensor "outdoor and indoor"
depende talaga sa heat loads.

inulit mo lang brian eh  Grin
Logged

-Conserve Water; Drink Beers
-Yesterday I did not even know how to spell engineer, today I am already one...
-LORD, Ty sa mga pagsubok na binibigay mo para maging handa ako sa mga biyayang darating..
The Philippine Electronics and Technology Forum
   

 Logged
Pages: [1]   Go Up
  Print  
 
Jump to:  


Related Topics
Subject Started by Replies Views Last post
pwede po ba ang 50hz d2?? SONY
Sony Televisions
niceguy812 8 789 Last post May 25, 2010, 01:48:49 PM
by GuDo
50Hz 60Hz
Absolute Beginner Technical Discussion
zaki 1 761 Last post August 19, 2008, 02:51:12 PM
by rdpzycho
air compressor
Electrical Device Repair (Electricians Forum)
kagore 3 927 Last post April 21, 2009, 07:34:41 PM
by ahlburuto
how to repair refrigeratot compressor?
Electrical Appliances
cassfa 4 960 Last post January 17, 2010, 11:18:16 PM
by ElektroniC8
Hiding the air conditioner compressor
Consumer Electronics, Appliances and Electronic Gadgets
johnnie707 1 249 Last post May 10, 2010, 03:33:06 PM
by DigitalMind
50hz vs. 60hz
Zilog Microcontrollers
mikel 3 129 Last post July 07, 2011, 11:38:28 AM
by mikel
Compressor/Limiter/Clipper circuit
Philippine Amateur Radio
duldog 3 390 Last post January 05, 2012, 05:17:40 PM
by DigitalMind
Powered by MySQL Powered by PHP Powered by SMF 1.1.15 | SMF © 2011, Simple Machines Valid XHTML 1.0! Valid CSS!