Author Topic: circuit breaker and wires  (Read 1230 times)
moira
Size AAA Battery
***

Pogi/Ganda Points: 0
Offline Offline

Posts: 68



« on: March 05, 2010, 12:51:18 PM »

gusto ko lang e confirm kung ano ang standard ampere rating ng breaker at ang number ng mga wires.
magdepende ba to sa mga loads?
pano ba yuun meron bang computation? halimbawa, ref, tv, aircon at mga bulbs, ano kaya ang specs ng breaker at wires ko?

sori po if hindi ko maipaliwanag ng mabuti, newbie lng kasi ako sa electronics and electrical.

sana meron tumulong....
Logged
The Philippine Electronics and Technology Forum
« on: March 05, 2010, 12:51:18 PM »

 Logged
I n s i d e r 2010
Diesel Generator
*

Pogi/Ganda Points: 99
Offline Offline

Gender: Male
Posts: 1618

matalino ka man ngayon ay mapagiiwanan ka rin


« Reply #1 on: March 05, 2010, 01:02:23 PM »

sis may katulad na ang post mo d2

pakihalungkat nalang po
Logged

ang PIKON ay laging TALO,tandaan nyo po yan mga kapatid. IRESPETO ang bawat isa!
ang PANLALAIT sa kapwa ay isang kasalanan na
pagbabayaran mo rin balang araw!
akhen
Diesel Generator
*

Pogi/Ganda Points: 41
Offline Offline

Gender: Female
Posts: 1080


"Learning is good but application is 100x better!"


« Reply #2 on: March 05, 2010, 01:15:32 PM »

sa residential po ba?

usually 4 na relay(ckt breaker) ang ginagamit:
1. main 60A
2. lights 15A
3. outlet 20A
4. ref 20A

kung may aircon mas maganda nakabukod din ang relay nya 20A.

yung TV kasama na sa outlet yun...
Logged

n!xau xixo
CR2032 Battery
**

Pogi/Ganda Points: 1
Offline Offline

Posts: 22


Ang SUPER HERO Na Pweding Arkilahin


« Reply #3 on: March 05, 2010, 03:01:56 PM »

gusto ko lang e confirm kung ano ang standard ampere rating ng breaker at ang number ng mga wires.
magdepende ba to sa mga loads?
pano ba yuun meron bang computation? halimbawa, ref, tv, aircon at mga bulbs, ano kaya ang specs ng breaker at wires ko?

sori po if hindi ko maipaliwanag ng mabuti, newbie lng kasi ako sa electronics and electrical.

sana meron tumulong....

size of wire:
1. minimum size of wire for lighting load = #14AWG, max. 12pcs. connected in one branch circuit.
2. minimum size of wire for power load (convenience outlet - C.O.) = #12AWG, max. 10pcs. connected in one branch circuit.
3. aircon (ACU) = depende sa specs ng compressor, in FLA - full load current (tingnan mo na lang yung label o sticker ng aircon), pero sinusunod pa rin yung minimum size of wire for ACU na #10AWG.

total load current ng residential +125%, dito na dedepende yung size of wire mo (feeder line / service intrance) at yung main breaker (AT).

sa mga branch circuit breaker naman, nearest to the AT.

ampacity of wire (based on 3wires in a single race way):
1. #14AWG = 15amperes (TW)
2. #12AWG = 20amperes (TW)
3. #10AWG = 30amperes (TW)
Logged
moira
Size AAA Battery
***

Pogi/Ganda Points: 0
Offline Offline

Posts: 68



« Reply #4 on: March 05, 2010, 03:51:07 PM »

size of wire:
1. minimum size of wire for lighting load = #14AWG, max. 12pcs. connected in one branch circuit.
2. minimum size of wire for power load (convenience outlet - C.O.) = #12AWG, max. 10pcs. connected in one branch circuit.
3. aircon (ACU) = depende sa specs ng compressor, in FLA - full load current (tingnan mo na lang yung label o sticker ng aircon), pero sinusunod pa rin yung minimum size of wire for ACU na #10AWG.

total load current ng residential +125%, dito na dedepende yung size of wire mo (feeder line / service intrance) at yung main breaker (AT).

sa mga branch circuit breaker naman, nearest to the AT.

ampacity of wire (based on 3wires in a single race way):
1. #14AWG = 15amperes (TW)
2. #12AWG = 20amperes (TW)
3. #10AWG = 30amperes (TW)


salamat sis sa reply. now i know pwede na akong mag umpisa.

sa residential po ba?

usually 4 na relay(ckt breaker) ang ginagamit:
1. main 60A
2. lights 15A
3. outlet 20A
4. ref 20A

kung may aircon mas maganda nakabukod din ang relay nya 20A.

yung TV kasama na sa outlet yun...

salamat din akhen.
Logged
moira
Size AAA Battery
***

Pogi/Ganda Points: 0
Offline Offline

Posts: 68



« Reply #5 on: March 05, 2010, 03:59:07 PM »

size of wire:
1. minimum size of wire for lighting load = #14AWG, max. 12pcs. connected in one branch circuit.
2. minimum size of wire for power load (convenience outlet - C.O.) = #12AWG, max. 10pcs. connected in one branch circuit.
3. aircon (ACU) = depende sa specs ng compressor, in FLA - full load current (tingnan mo na lang yung label o sticker ng aircon), pero sinusunod pa rin yung minimum size of wire for ACU na #10AWG.

total load current ng residential +125%, dito na dedepende yung size of wire mo (feeder line / service intrance) at yung main breaker (AT).

sa mga branch circuit breaker naman, nearest to the AT.

ampacity of wire (based on 3wires in a single race way):
1. #14AWG = 15amperes (TW)
2. #12AWG = 20amperes (TW)
3. #10AWG = 30amperes (TW)



by the way sis, ano ung (TW)? at ung (AT)? sa itaas?thanks in advance
Logged
n!xau xixo
CR2032 Battery
**

Pogi/Ganda Points: 1
Offline Offline

Posts: 22


Ang SUPER HERO Na Pweding Arkilahin


« Reply #6 on: March 05, 2010, 04:10:12 PM »



by the way sis, ano ung (TW)? at ung (AT)? sa itaas?thanks in advance

sorry nga pala,

TW - type lang ito ng wire, marami kasing klase yan sir, merong TW, THW, THHN. ito yung mga kalimitang ginagamit sa mga residential electrical installation. magkakaiba ang mga wire ampacity nito. pero basically TW ang ginagamit kasi mura sya.

AT - ampere trip ng circuit breaker. ito ang term na ginagamit sa mga circuit breaker.
estimate the fuse/CB rating based on wire ampacity...and estimate the wire size/ampacity based on loads.  madalas yata jan galing ang sunog from electrical fault kasi nasunog na ang wire. di pa rin nagtrip ang protection kasi oversized.
kailangan magkakalapit lang silang lahat.
Logged
Co0LėT♥
Hydroelectric
***

Pogi/Ganda Points: 362
Offline Offline

Gender: Female
Posts: 3330



« Reply #7 on: March 05, 2010, 04:14:52 PM »

TW =  type of  insulation

yung AT is at command hehehe  Grin Grin Grin
Logged

Simpler designs are usually better.
luis
CR2032 Battery
**

Pogi/Ganda Points: 0
Offline Offline

Gender: Male
Posts: 22



« Reply #8 on: July 25, 2010, 01:59:28 PM »

TW-thermoplastic wire (kind/type of insulation) AT-ampere trip (rated current of the C.B)
Logged

Ang kayamanan ay palamuti lamang sa ating buhay,hindi maidadala sa kamatayan.,kaya habang buhay ka pa,ibahagi mo na lang sa iba..kaysa nman mapunta sa wala.. Smiley)
The Philippine Electronics and Technology Forum
   

 Logged
Pages: [1]   Go Up
  Print  
 
Jump to:  


Related Topics
Subject Started by Replies Views Last post
Koten o Omni Circuit breaker
Electrical Circuits and Devices
mangkanor 7 2545 Last post July 16, 2008, 08:04:54 AM
by tyrap
tanong tungkol sa fuse/circuit breaker « 1 2 ... 5 6 »
Electrical Circuits and Devices
Siramiko 117 8165 Last post May 08, 2010, 06:08:51 PM
by valtomotive
HELP: circuit breaker sparking!
Electrical Device Repair (Electricians Forum)
tikbalang 12 1940 Last post June 02, 2008, 08:04:46 PM
by ahlburuto
Aircon without circuit breaker « 1 2 3 »
Electrical Engineering Board
paranz 41 4404 Last post July 31, 2008, 04:51:20 PM
by paranz
For REE/PEE: Substation Air Circuit Breaker
Electrical Engineering Board
j_cash777 9 871 Last post March 05, 2010, 01:30:48 PM
by winn1971
ilang ampers na circuit breaker gagamitin
Electrical Circuits and Devices
pinoycobra 11 1011 Last post March 25, 2010, 09:39:53 AM
by ahlburuto
8kw shower heater: no dedicated breaker and underrated wire/breaker « 1 2 »
Electrical Circuits and Devices
scubarat 28 1186 Last post August 19, 2010, 07:43:48 PM
by iyo karpo
Powered by MySQL Powered by PHP Powered by SMF 1.1.15 | SMF © 2011, Simple Machines Valid XHTML 1.0! Valid CSS!