Author Topic: tanong tungkol sa fuse/circuit breaker  (Read 8170 times)
pete
Hydroelectric
***

Pogi/Ganda Points: 464
Online Online

Gender: Male
Posts: 3986



« Reply #100 on: March 05, 2010, 06:29:23 PM »


something wrong kung palaging nagti-trip ang breaker.  Huh
over load
Logged

CASTILLO ELECTRONICS
1032 Kamias St. NAPICO PASIG
The Philippine Electronics and Technology Forum
« Reply #100 on: March 05, 2010, 06:29:23 PM »

 Logged
Co0LėT♥
Hydroelectric
***

Pogi/Ganda Points: 362
Offline Offline

Gender: Female
Posts: 3330



« Reply #101 on: March 05, 2010, 06:40:24 PM »

ang ganda ni dadi coolet ah


loko loko  Grin Grin Grin
Logged

Simpler designs are usually better.
de PatAtas
Diesel Generator
*

Pogi/Ganda Points: 319
Offline Offline

Gender: Male
Posts: 1267


' The unbreakable


« Reply #102 on: March 05, 2010, 06:57:55 PM »

 Grin
Logged

' there are many different ways to love..
Co0LėT♥
Hydroelectric
***

Pogi/Ganda Points: 362
Offline Offline

Gender: Female
Posts: 3330



« Reply #103 on: March 05, 2010, 06:59:43 PM »

^ kePyaS bakit sa inuduro ka naghihilamos?  Grin
Logged

Simpler designs are usually better.
de PatAtas
Diesel Generator
*

Pogi/Ganda Points: 319
Offline Offline

Gender: Male
Posts: 1267


' The unbreakable


« Reply #104 on: March 05, 2010, 07:13:29 PM »

 ' ala kasing tubig da lababo eh....ala tubig ala kuryenti ano bang
 nangyayari sa PiliPinas?
Logged

' there are many different ways to love..
n!xau xixo
CR2032 Battery
**

Pogi/Ganda Points: 1
Offline Offline

Posts: 22


Ang SUPER HERO Na Pweding Arkilahin


« Reply #105 on: March 05, 2010, 08:15:36 PM »

something wrong kung palaging nagti-trip ang breaker.  Huh

over load

not all the time naman dahil sa overload case, yung nasa workshop o repair ng mga industrial motors, nagkakaroon sila ng tripping ng CB because of shorted motor. kaya advice lang na e check yung CB para sa posibling damage ng CB. kahit minsan sa mga electronics repair shop, hindi maiiwasan sa pagsaksak mo ng unit ay shorted pala.
Logged
pete
Hydroelectric
***

Pogi/Ganda Points: 464
Online Online

Gender: Male
Posts: 3986



« Reply #106 on: March 06, 2010, 10:05:31 AM »

not all the time naman dahil sa overload case, yung nasa workshop o repair ng mga industrial motors, nagkakaroon sila ng tripping ng CB because of shorted motor. kaya advice lang na e check yung CB para sa posibling damage ng CB. kahit minsan sa mga electronics repair shop, hindi maiiwasan sa pagsaksak mo ng unit ay shorted pala.
so over load parin once na may short diba?
Logged

CASTILLO ELECTRONICS
1032 Kamias St. NAPICO PASIG
iyo karpo
Lead Acid Battery
*******

Pogi/Ganda Points: 17
Offline Offline

Posts: 869


« Reply #107 on: March 06, 2010, 10:40:02 AM »

If it's an ordinary breaker, then there is overcurrent condition (current greater than the circuit breaker AT rating).

If it is a special breaker GFCB (Ground Fault Circuit Breaker) or AFCB (Arc Fault Circuit Breaker), then overcurrent is not the only cause for tripping.
Logged
n!xau xixo
CR2032 Battery
**

Pogi/Ganda Points: 1
Offline Offline

Posts: 22


Ang SUPER HERO Na Pweding Arkilahin


« Reply #108 on: March 07, 2010, 09:46:37 PM »

If it's an ordinary breaker, then there is overcurrent condition (current greater than the circuit breaker AT rating).

If it is a special breaker GFCB (Ground Fault Circuit Breaker) or AFCB (Arc Fault Circuit Breaker), then overcurrent is not the only cause for tripping.


yup, yun po bang GFCB (Ground Fault Circuit Breaker) = sa ELCB (Earth Leakage Circuit Breaker)?
Logged
iyo karpo
Lead Acid Battery
*******

Pogi/Ganda Points: 17
Offline Offline

Posts: 869


« Reply #109 on: March 08, 2010, 04:46:11 AM »

yup, yun po bang GFCB (Ground Fault Circuit Breaker) = sa ELCB (Earth Leakage Circuit Breaker)?

that's right. ELCB noong araw, ngayong maraming na ang nakoryente sa banyo at alababo dito North America, tinawag na nilang GFCB.
Logged
rage3657
Size AAA Battery
***

Pogi/Ganda Points: 2
Offline Offline

Posts: 78


« Reply #110 on: March 08, 2010, 04:34:04 PM »

If you are operating an industrial plant that require coordination protection, you use high kaic rated fuse or breaker.

If your application is a residential unit with no strict requirement for a maintenance program, use a low kaic breaker or fuse.


hindi ba depende un sa duty ng CB may mababa may mataas na interrup capacity sa isang installation. kasi ang purpose nun is to localize the problem. so sa ind. plant may mababa rin. mas mababa sa branch mataas sa main para kung may problem sa isang portion dun lang, kasi kung napataas ang kAIC sa branch kesa sa main shutdown buong plant.. nakupow malaking hayop un.. dapat proper coordination.
Logged
iyo karpo
Lead Acid Battery
*******

Pogi/Ganda Points: 17
Offline Offline

Posts: 869


« Reply #111 on: March 08, 2010, 09:20:11 PM »

hindi ba depende un sa duty ng CB may mababa may mataas na interrup capacity sa isang installation. kasi ang purpose nun is to localize the problem. so sa ind. plant may mababa rin. mas mababa sa branch mataas sa main para kung may problem sa isang portion dun lang, kasi kung napataas ang kAIC sa branch kesa sa main shutdown buong plant.. nakupow malaking hayop un.. dapat proper coordination.

That's right. We call that selective coordination, isolating a fault condition. Coordination study is one of the electric utility's requirement before commissioning a distribution system. Ayaw nilang madamay pag may fault sa planta.
Logged
Co0LėT♥
Hydroelectric
***

Pogi/Ganda Points: 362
Offline Offline

Gender: Female
Posts: 3330



« Reply #112 on: March 08, 2010, 09:53:22 PM »

That's right. We call that selective coordination, isolating a fault condition. Coordination study is one of the electric utility's requirement before commissioning a distribution system. Ayaw nilang madamay pag may fault sa planta.

dba normal naman yan sa mga plant? hindi ka kakabitan ng power pag isa lang breaker mo sa lahat ng makina hehe  Grin
Logged

Simpler designs are usually better.
iyo karpo
Lead Acid Battery
*******

Pogi/Ganda Points: 17
Offline Offline

Posts: 869


« Reply #113 on: March 09, 2010, 10:33:44 AM »

dba normal naman yan sa mga plant? hindi ka kakabitan ng power pag isa lang breaker mo sa lahat ng makina hehe  Grin

Normal sa planta ang fault, ayaw lang nilang masira ang boung power system dahilang sa short circuit ng isang planta.
Logged
valtomotive
CR2032 Battery
**

Pogi/Ganda Points: 0
Offline Offline

Gender: Male
Posts: 19



« Reply #114 on: May 07, 2010, 07:27:26 PM »

pwede bang e combine ang electric welding machine at cement mixer 3 phase motor sa 100 amp breaker inde ba mag ti trip pag nag sabay ang gamit
Logged
iyo karpo
Lead Acid Battery
*******

Pogi/Ganda Points: 17
Offline Offline

Posts: 869


« Reply #115 on: May 08, 2010, 09:29:40 AM »

pwede bang e combine ang electric welding machine at cement mixer 3 phase motor sa 100 amp breaker inde ba mag ti trip pag nag sabay ang gamit

pag ang combined starting amperes lampas sa 100A siguradong mag trip.
Logged
jacks
Nuclear Reactor
****

Pogi/Ganda Points: 189
Offline Offline

Posts: 4272



« Reply #116 on: May 08, 2010, 10:20:55 AM »

Mas magandang magkahiwalay breaker nila kasi masyado dynamic duty cycle ng wmachine. Pwedeng magtrip(magkasabay) o hindi bumitaw ang breaker kung cement mixer lang ang load kapag may problema .
Logged
valtomotive
CR2032 Battery
**

Pogi/Ganda Points: 0
Offline Offline

Gender: Male
Posts: 19



« Reply #117 on: May 08, 2010, 06:08:51 PM »

salamat sa mga info 4 months pa lang ako sa maintenance kung ano ano na pinapagawa sakin hehe pati pag wiring ng mga machine tools sakin pinapagawa medyo natuto na din kahit konti hehe 
Logged
The Philippine Electronics and Technology Forum
   

 Logged
Pages: 1 ... 4 5 [6]   Go Up
  Print  
 
Jump to:  


Related Topics
Subject Started by Replies Views Last post
tanong tungkol sa I2C « 1 2 »
Computer Interfacing and Digital Communications
Siramiko 20 3031 Last post February 09, 2008, 06:54:35 PM
by paranz
tanong tungkol sa stepper motor?
Electrical Circuits and Devices
marklimson 3 790 Last post September 04, 2008, 08:42:06 AM
by maldihtah13
Tanong lang po tungkol sa zilog
Zilog Microcontrollers
mikel 6 1134 Last post November 18, 2008, 09:33:34 PM
by mikel
tanong tungkol sa IP address « 1 2 »
Computer Programming/Software Engineering
Siramiko 26 2688 Last post March 05, 2010, 08:41:01 PM
by rdpzycho
8kw shower heater: no dedicated breaker and underrated wire/breaker « 1 2 »
Electrical Circuits and Devices
scubarat 28 1186 Last post August 19, 2010, 07:43:48 PM
by iyo karpo
Tanong ko po tungkol sa Wattage / Power Consumption.
Electrical Appliances
Similya 2 133 Last post July 24, 2011, 09:17:38 PM
by dongski
tanong tungkol sa power supply
Absolute Beginner Technical Discussion
wrath 4 150 Last post November 27, 2011, 09:47:37 PM
by wrath
Powered by MySQL Powered by PHP Powered by SMF 1.1.15 | SMF © 2011, Simple Machines Valid XHTML 1.0! Valid CSS!